You need to be careful here ... there are two dimming systems which sound similar but are very different!
In the entertainment work there has been for many years a system of 0-10V control where the controller sends an analogue voltage to the dimmer unit & it controls the lamps. In tis scheme 0V = fully off & 10V = fully on, with proportional control inbetween ... ie 5V = 50V.
There is also another system which first originated for fluorescent lights which is the 1-10V system. This is very different to 0-10V & they are not compatible! With the 1-10V system the lighting fixture supplies the voltage between the two terminals - when the terminals are open circuit the voltage will be 10V. The controller applies a 'resistance' between these to pull a current, the more current that is pulled, (ie. the lower the resistance) the more the voltage falls and the more the fixture dims.