I am posting this in this forum to get feedback more from an Engineering stand point.
The issues on this job grow day to day. Here is the latest issue.
We have 0-10 volt DC dimming with LED lights. The wiring method that was chosen was 12/4 MC. Two conductors carry the 277 volt power and neutral and the other two are the 0-10 volt DC.
These drivers in the LED lights source the 0-10 volt DC. The dimmers in each room are just an on/off button with a slider that inserts resistance in the 0-10vdc line. No resistance (10vdc) is full brightness, increase the resistance till you get 0 volts or short the wires together and you have full dimming.
I am getting a vibrating/pulsing in the lights in certain rooms. But in certain rooms with the same amount of lights i am not getting this effect...? I have been able to correct it by running low voltage wire for the 0-10vdc and abandoning the two extra conductors in the MC for the 0-10vdc.
What I am trying to figure out is why this is happening? Is the AC side inducing and interfering with the 10 Vdc side? Why only some rooms and not all with the same exact set up? It also intensifies with longer runs and more lights.
One other interesting thing. I disconnected the 0-10 volt DC from all three lights in one of the rooms and just left the two conductors in the MC used for the dimming circuit connected in and out of each light. I then removed those same two wires from the dimmer so they were connected to nothing at each end, at this point they were just two extra wires through the MC about 30' long. I took some "AC" voltage readings with a High and Low impedance meter and had 30-60 Volts AC between them and 50 - 100 Volts AC to ground....! Regardless of which meter i used i definitely had significant voltages on those wires.
Also, some of the 4 wire MC that was used was MC light (aluminum jacket), some of it was a heavier steal jacket. When the MC sheath was stripped back some of the brands twist their conductors inside and some are straight. Could any of this affect why it is happening in some of the rooms?
The issues on this job grow day to day. Here is the latest issue.
We have 0-10 volt DC dimming with LED lights. The wiring method that was chosen was 12/4 MC. Two conductors carry the 277 volt power and neutral and the other two are the 0-10 volt DC.
These drivers in the LED lights source the 0-10 volt DC. The dimmers in each room are just an on/off button with a slider that inserts resistance in the 0-10vdc line. No resistance (10vdc) is full brightness, increase the resistance till you get 0 volts or short the wires together and you have full dimming.
I am getting a vibrating/pulsing in the lights in certain rooms. But in certain rooms with the same amount of lights i am not getting this effect...? I have been able to correct it by running low voltage wire for the 0-10vdc and abandoning the two extra conductors in the MC for the 0-10vdc.
What I am trying to figure out is why this is happening? Is the AC side inducing and interfering with the 10 Vdc side? Why only some rooms and not all with the same exact set up? It also intensifies with longer runs and more lights.
One other interesting thing. I disconnected the 0-10 volt DC from all three lights in one of the rooms and just left the two conductors in the MC used for the dimming circuit connected in and out of each light. I then removed those same two wires from the dimmer so they were connected to nothing at each end, at this point they were just two extra wires through the MC about 30' long. I took some "AC" voltage readings with a High and Low impedance meter and had 30-60 Volts AC between them and 50 - 100 Volts AC to ground....! Regardless of which meter i used i definitely had significant voltages on those wires.
Also, some of the 4 wire MC that was used was MC light (aluminum jacket), some of it was a heavier steal jacket. When the MC sheath was stripped back some of the brands twist their conductors inside and some are straight. Could any of this affect why it is happening in some of the rooms?