Can 300v rated CL3 Speaker wire be used for the Purple and Grey connection from a wall switch to a dimmable LED Fixture?
I only ask because I have some of that laying around.
I touched on this before but never got a good feeling about it.
The Power and the 0-10v dimming leads share the same compartment in the Fixture with no divider.
The Wall Dimmer has the 120v power, switchleg and purple and grey dimming leads coming out of it.
MC Cable is daisy chained to 4 fixtures and a 12/4 MC cable is ran down to the switch.
Can CL3 2 conductor cable be pulled fixture to fixture and down the wall into the existing switch box and be legal?
Not sure where the dividing line is between sharing 120v and Low Voltage cable in the same enclosure where there is no divider or if that's even acceptable at all.