0-10V Dimming Problems

Status
Not open for further replies.

jimdavis

Senior Member
We're just finishing up a huge job- a public venue with a high-end theatrical lighting system. I have a few circuits that exhibit flickering while dimming up or down. The fixtures are LED and controlled via 0-10V from dimmer racks. I have other circuits in the building which are using the same fixtures and dimming configuration and they work just fine. The power and 0-10V conductors are run in separate raceways. The building has well over a thousand lighting circuits and I've worked through a lot of issues but this one is getting the better of me. Any thoughts or ideas?
 

JFletcher

Senior Member
Location
Williamsburg, VA
Wow, big building.

wag, but with that many devices and circuits, I have to wonder if you've gotten a few bad ones (devices or bulbs) from the mfgs. Wouldnt be out of the realm of possibility.
 

Electric-Light

Senior Member
is the troubled one and well working one using the same controller?

Lighting dimming is done with a potentiometer to pull the voltage down. So the first step in trouble shooting is to disconnect the dimming system from 0-10v and sweep from maximum to minimum with the most basic 0-10v dimmer attached across 0-10v wiring. You only need to connect the dimming control wires.

Theatrical dimming is often done with a variable voltage power supply feeding 0-10v into light fixture. Use a ghetto cheap analog DC volt meter(it provides low enough impedance to act as a load) and place it across 0-10v terminals on the dimming system with nothing connected. If you see it providing 0-10v with no light fixture, then you have a sourcing theatrical dimming system. Some dimmers are capable of feeding into theatrical load as well as sinking lighting loads, otherwise, they'll fight each other.

A mismatch requires an interface box. In this case, call Lutron. They'll explain what you'll need.
 
Last edited: