Frequently LED fixtures seem to come standard with 0-10v dc dimming. I haven’t investigated, obviously, but what are the power requirements for these supplies? Could I use common dry cell batteries to supply this voltage? Is 0 volts full bright?
most everything comes with 0-10 dimming anymore.
it's near impossible to make a california compliant installation without it.
take the 0-10 wires apart. fixture is full bright.
short the 0-10 wires together. fixture is full dim.
some luminaries seem to have a 0-10 volt set of dimming leads
on the ballast. lutron however, it might be their eco bus. digitally
adressable devices. can put 64 of them on a serial bus. wires coming
out of device are same gauge and coloring as 0-10. mixing them
with 0-10 volt lighting will cause much entertainment and profanity
as the system is attempted to be programmed.
if you have lutron fixtures, take one out of the box, stick the power
leads into an extension cord, so it lights up, and short the "0-10"
dimming leads togeather. if the light goes dim, it's 0-10.... if they
don't, it's eco. wire accordingly.
assuming the boxes the luminaries came in are correctly marked
should be done at your own peril. i've see two situations now
where boxes marked "0-10" contained eco drivers. the second time,
it was discovered at 1:15 in the morning, and took till 5 am to fix.
a fun time was had by all.