0-10V Dimming

Status
Not open for further replies.

PFraga

New User
Location
San Diego
Occupation
Electrician
I have a project replacing 86 flourescent 2x2 troffers with 43 LED 0-10Volt 2x2s. the 86 fixtures run off of 4 circuits (120V) with four 3&4way switch locations controlling a lighting contactor.

What's the best plan of attack? Where can I intercept the circuit to install the 0-10V power pack? Do I need one for all 4 circuits, or just one south of the contactor? Will I have issues with the lighting contactor, and need one compatible with the new system? Would a remote power pack work here instead of running low voltage wire to the switch locations?
 

jusme123

Senior Member
Location
NY
Occupation
JW
Use MC Luminary cable, it has the grey/purple LV dimming wires inside with the power wires

5AD89383-8610-4E0C-8C50-F8F8A9294BA5.jpeg
 