0-10v from Lutron dimming panel to Lighting

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
running a neutral and dimmed hot from Lutron dimming panel to light. Does it have to be run in conduit?
AFAIK. those two wires in the Lutron system (but maybe not in a Lutron substitute) are rated and identified as Class 2.
If the applicable codes require Class 2 circuits to be in raceway, then you are stuck, but I do not think that is likely.
 

n1ist

Senior Member
Location
Massachusetts
Occupation
Principal Electrical Engineer
Neutral and dimmed hot sound like class 1 to me. 0-10v (purple and grey) can be class 1 or 2 depending on the setup and dimming panel.
 