dcspector
Senior Member
- Location
- Burke, Virginia
Correct me if I am wrong. Example: Elevator disconnect 200 amp OCPD. For whatever reason they installed 750 kcmil Al with a #4 Al EGC. VD is not an issue. They could have used per 310.16 250 kcmil AL with a #4 Al EGC per 250.122. I took The circular mils 750 divided by 250 circular mils=3.0 then #4 EGC circular mils(41740) x 3.0=125220 circular mils which per Tbl. 8 that is greater than a 1/0 so one would use 2/0 EGC.
Thanks all.