ivsenroute
Senior Member
- Location
- Florida
Just got some preliminary information that tomorrow I am inspecting 2 separate 1,000 foot runs of the above for a 12.5kvac feed to a 150kVa xfmr.
Anyway they are down approximately 48" in a trench and have the 4" standoffs approximately 10' apart. The 3" is suppose to get concrete encasement of a 4" minimum top and bottom per specs.
I have 2 concerns, questions:
1) Maximum space between supports is really a moot point since it is buried raceway and will be concrete encased, HOWEVER, with the standoffs at 10' apart I am concerned that the middles with dip down below the specified encasement but I don't see how I can make the horizonal supports apply. Again, just a concern. How do you set up these runs for encasement?
2) There is no exclusion for 352.44 as far as expansion fitting are concerned but what good will they do once the concrete is encased?
The fact that there are 1,000 feet between pulls in a straight run concerns me with the expansion fittings, even at the minimum 5 degree change in temp.
The 2005 NEC applies
Anyway they are down approximately 48" in a trench and have the 4" standoffs approximately 10' apart. The 3" is suppose to get concrete encasement of a 4" minimum top and bottom per specs.
I have 2 concerns, questions:
1) Maximum space between supports is really a moot point since it is buried raceway and will be concrete encased, HOWEVER, with the standoffs at 10' apart I am concerned that the middles with dip down below the specified encasement but I don't see how I can make the horizonal supports apply. Again, just a concern. How do you set up these runs for encasement?
2) There is no exclusion for 352.44 as far as expansion fitting are concerned but what good will they do once the concrete is encased?
The fact that there are 1,000 feet between pulls in a straight run concerns me with the expansion fittings, even at the minimum 5 degree change in temp.
The 2005 NEC applies