1 1/4” threaded grounding hub

Status
Not open for further replies.

Shockedby277v

Senior Member
Location
Michigan
I need to choke my 1 1/4” EMT that I used for my 3/0 grounding electrode conductor. I am having a hard time finding a 1 1/4” threaded conduit grounding hub. Besides a bond bushing does anyone know another method or know where to get a 1 1/4” grounding hub? 1” are fairly common.


D7A928B7-6A1F-44DD-9A97-59D0109FBECA.jpeg
 
If you can't locate one there are other ways around this. Kind of clunky but compliant to just run a jumper or loop the GEC through to a standard ground clamp on the conduit.
 