1/2" emt connector

Status
Not open for further replies.

iwirehouses

Senior Member
I've seen them before but am currently unable to find a 1/2" emt to romex connector. This connector eliminates the need to have a junction box when dropping a run of emt down a wall from a source that is romex. I've heard you can just use a regular emt box connector at the end of the emt just to provide a smooth edge and that you don't actually need a junction box. Is this true?
 
Re: 1/2" emt connector

You may need one of these according to 334.15(C)as Ryan pointed out.


c3_8600im.jpg



Here's the link for the fitting:

http://www.aifittings.com/c_3.htm#8600
 
Re: 1/2" emt connector

Lets see if i get blasted by this one.

Use a romex connector, strip the wire the proper length. use a rigid coupling and screw the emt connector into that.
 
Re: 1/2" emt connector

someone correct me, but I think that this connection needs to remain accessable.

Ryan jump in here if you will .
 
Re: 1/2" emt connector

The fitting (a from-to) shown above is one way...another way is to use an EMT conn./rigid coupling/RX conn. set-up.
Sometimes you go with what you have laying around :D
 
Re: 1/2" emt connector

Originally posted by jbwhite:
Lets see if i get blasted by this one.

Use a romex connector, strip the wire the proper length. use a rigid coupling and screw the emt connector into that.
That works for me. Don't know what the "others" will say.


Trevor
 
Re: 1/2" emt connector

Originally posted by ty:
Can you strip NM and run it through conduit?

And are you guys siting 2005??
That is what I am saying.

But I cant find the part where, and i think it is there, that the connection has to remain accessable.

If you stip NM then you have 90deg c thhn.
 
Re: 1/2" emt connector

Don't forget, you can use a plastic bushing on the end of the emt also.
I don't think stripping the cover off of the nm is a good idea as it is listed to be installed as a cable assembly.
 
Re: 1/2" emt connector

All you would need is a pop on bushing, you do not need a clamp or securing type of fitting for this per the wording of 334.15(C)

NM cable used on a wall of an unfinished basement shall be permitted to be installed in a listed conduit or tubing. Conduit or tubing shall utilize a nonmetallic bushing or adapter at the point the cable enters the raceway. Metal conduit and tubings and metal outlet boxes shall be grounded.
Notice the "or".

Roger
 
Re: 1/2" emt connector

Originally posted by jbwhite:

If you stip NM then you have 90deg c thhn.
Jb, although this may be true we can't use this reasoning. The conductors are not identified as required by 310.11(A).

Roger
 
Re: 1/2" emt connector

Originally posted by ty:
Roger,
(HI :) )

That must be 2005.

2002 states 'fitting', which I'd agree the snap-in bushing would be :) You are right, I was quoting from the 05.

Roger
 
Re: 1/2" emt connector

Actually, we're all sick :(

How 'bout you?

Anyway, DE still hasn't adopted 2005, so I don't open it as much. Some counties in MD have, but they have ammendments.
 
Re: 1/2" emt connector

Originally posted by roger:
Originally posted by jbwhite:

If you stip NM then you have 90deg c thhn.
Jb, although this may be true we can't use this reasoning. The conductors are not identified as required by 310.11(A).

Roger
The outer cable insulation has the markings, we are just gonna strip off a bit to drop to an rec.
IMHO the labeling requirements are met.
 
Re: 1/2" emt connector

Jb,
we are just gonna strip off a bit to drop to an rec.
strip the wire the proper length. use a rigid coupling and screw the emt connector into that.
I can live with that, but that is different than
If you stip NM then you have 90deg c thhn.
. as a blanket statement :)

Roger

[ January 12, 2006, 07:12 PM: Message edited by: roger ]
 