Exactly. Why ever buy a fan rated pancake box?Originally posted by electricmanscott:
If you have a standard box just drive the fan mounting screws into the wood that the box is mounted to.
Answer- to satisfy all the electrical inspectors that neither visit here or similar sites, nor bother with a code book since they passed a jman test back in 1963. And they have that attitude " This is how I like it done". They still exist. We got at least one where I'm at.Exactly. Why ever buy a fan rated pancake box?
It does?Originally posted by mpd:
look at it from the inspectors side, a fan rated pancake box takes the guess work out of how the contractor will support the fan,
Larry is there a local amendment to the NEC?Originally posted by LarryFine:
In this area, city inspectors remark the quantity of fan boxes during rough-in inspection, and make sure there is not a greater number ofr fans installed at final.
Support the fan from the structure and the need for a fan box is not applicable.314.27 (D) Boxes at Ceiling-Suspended (Paddle) Fan Outlets. Where a box is used as the sole support of a ceiling-suspended (paddle) fan, the box shall be listed for the application and for the weight of the fan to be supported. The installation shall comply with 422.18.
Whatcha got against roofing nails?Originally posted by mpd:
...he does not have to worry about a fan being supported with...roofing nails...
Would you care to pass this method along? I've used pancakes and screwed right through the box and into the framing, which is legal. Mostly I use a Westinghouse plastic fan box or a "saddle box". I've never known a way to use a regular 4" octagon in a compliant way for fans. Fill me in...Originally posted by j_erickson:
I have a certain way of installing a fan on a 4" octagon where it is completely legal, and for me is better and faster.
Scott,If you have a standard box just drive the fan mounting screws into the wood that the box is mounted to
If you mount the fan to the building's structure, you can use whatever type of box pleases you. It doesn't need to be fan rated. You only need a fan rated box if you're supporting the fan directly off that box.Originally posted by goldstar:
Scott,If you have a standard box just drive the fan mounting screws into the wood that the box is mounted to
I'm not sure if that is correct. I think the pancake boxes that are rated for ceiling fans have 10/32 screws as a means of mounting fan supports whereas std. pancake boxes use 8/32's for mounting of the supports irespective of whether you attach the base to a ceiling rafter.
Phil,
Gold Star Electric
That is correct but was referring to the box mounting screwsIf you mount the fan to the building's structure, you can use whatever type of box pleases you. It doesn't need to be fan rated. You only need a fan rated box if you're supporting the fan directly off that box.