sparkkey
New member
- Location
- Los Angeles, CA, USA
Hello,
I've seen this topic danced around on several boards, and I can't find a thread specific to this scenario, so I will just put it out there for commenting:
(being asked in the spirit of UL508A acceptability)
There is a 480 VAC 3-phase electrical panel that has door-interlocked Fusible disconnect with 200A fuses feeding a 75HP variable frequency drive with a MAX AMP rating of 168A.
This same 200A fusible disconnect is ALSO feeding a SECOND, small 1/3HP motor through a fuse block with 3 amp fuses + contactor + overload.
Question:
Lets assume for the sake of argument that the 200A fuses are sized correctly for the VFD, and the circuit current is in an acceptable amp range with or without the 1/3HP motor running.
Is it ok for the 200 amp fusible disconnect be used as the both the feeder to the 1/3HP motor as well as the protection for the drive, where both devices share the same 200A fused circuit?
...OR must the branch circuits be separated so that only one set of fuses is connected to each motor circuit (200A on one, 3A on the other) thereby requiring a third protection device (MCCB or Fusible disconnect) that becomes the feeder to both the 200A fuses for the VFD and the 3A fuses for the 1/3HP motor?
Make sense?
Thanks!
-JP
I've seen this topic danced around on several boards, and I can't find a thread specific to this scenario, so I will just put it out there for commenting:
(being asked in the spirit of UL508A acceptability)
There is a 480 VAC 3-phase electrical panel that has door-interlocked Fusible disconnect with 200A fuses feeding a 75HP variable frequency drive with a MAX AMP rating of 168A.
This same 200A fusible disconnect is ALSO feeding a SECOND, small 1/3HP motor through a fuse block with 3 amp fuses + contactor + overload.
Question:
Lets assume for the sake of argument that the 200A fuses are sized correctly for the VFD, and the circuit current is in an acceptable amp range with or without the 1/3HP motor running.
Is it ok for the 200 amp fusible disconnect be used as the both the feeder to the 1/3HP motor as well as the protection for the drive, where both devices share the same 200A fused circuit?
...OR must the branch circuits be separated so that only one set of fuses is connected to each motor circuit (200A on one, 3A on the other) thereby requiring a third protection device (MCCB or Fusible disconnect) that becomes the feeder to both the 200A fuses for the VFD and the 3A fuses for the 1/3HP motor?
Make sense?
Thanks!
-JP