1/4 HP , 120 v motor overload ?

Status
Not open for further replies.
Is overload protection required on a ex-fan 1/4 HP , not thermally protected , continuous duty , not automatically started ex-fan motor ?
Not impedance protected either (mostly shaded pole motors but not normally for ones that large)?

Answer is yes if no other protection is involved.
 