1.4KW Electric Tankless waterheater

Status
Not open for further replies.

wmeek

Senior Member
Location
Texas
Occupation
Electrician
If you install a 20A single outlet under a sink for a tankless waterheater 1.4kw that plugs in , does it have to be gfci on commercial project
 

iwire

Moderator
Staff member
Location
Massachusetts
If you install a 20A single outlet under a sink for a tankless waterheater 1.4kw that plugs in , does it have to be gfci on commercial project

If it is 120 volt and in an area that requires GFCI you will have to provide it.

The exceptions for single receptacles are gone.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If you install a 20A single outlet under a sink for a tankless waterheater 1.4kw that plugs in , does it have to be gfci on commercial project
Is this really a tankless water heater or just a very small tank? 1.4kw cannot heat more than a trickle, IMHO.
 