All the following presumes these are ballasted lights, not say old incandescent (that would be nuts in 2024!).I have (36) 277V - 1kVA lights
Article 215 has the rules for calculating a feeder aka the "circuit feeding the panel".Would I calculate the circuit feeding the panel with 36,000W
So you need to go look at the nameplate of these '1000W' balasts and see how many amps they use at 277V, not the output watts of the fixture. Here is a sample data sheet (from 1000W MH lihgts used for sports area lighting)An outlet supplying luminaire(s) shall be calculated based
on the maximum volt-ampere rating of the equipment
and lamps for which the luminaire(s) is rated.
220.18(B) specifically requires nameplate current for LED drivers & Ballasted lights220.14 (D) Luminaires. says
An outlet supplying luminaire(s) shall be calculated based on the maximum volt-ampere rating of the equipment and lamps for which the luminaire(s) is rated.
310.15(E)To make sure its balanced I could figure the maximum imbalance .. so 12 circuits will balance.
I would argue that for most applications anything other than LED would be nuts in 2024, and I would include sports lighting in the list of applications where LED is appropriate.All the following presumes these are ballasted lights, not say old incandescent (that would be nuts in 2024!).
Seems to still be common to use HID in grow houses as questions involving HID issues that come up on sites like this often are involving grow houses.I would argue that for most applications anything other than LED would be nuts in 2024, and I would include sports lighting in the list of applications where LED is appropriate.
Agreed I think now in 2024 they got it worked out.I would argue that for most applications anything other than LED would be nuts in 2024, and I would include sports lighting in the list of applications where LED is appropriate.
.
There was also the problem of random lights turning purple mid game. .
I would argue that for most applications anything other than LED would be nuts in 2024, and I would include sports lighting in the list of applications where LED is appropriate.
HPS actually typically has a higher lumens per watt than LED, although HPS is omnidirectional so you need a reflector and there will be some losses there. Not sure how it typically works out for "delivered" lumens per watt.Seems to still be common to use HID in grow houses as questions involving HID issues that come up on sites like this often are involving grow houses.
Better lighting qualities for growing plants? IDK but kind of assuming that is the case.
With modern PFC power supplies I dont consider those things to be an issue anymore.310.15(E)
When considering current carrying conductors, triplen harmonics on Wye xfmr Neutral loads are CCC's regardless of balanced loads.
310.14(A)(3)
Informational note paragraph (2), describes harmonic load that overheat terminations. So load should not max ampacity, after the continuous factor x 1.25.
4.1A x 4 lights x 1.25 continuous = 20.5A
The industry practice for harmonics typically upsizes the neutral, in this example to a #10cu.
Does that include unlisted equip, with no FCC testing, which everyone buys from Amazon?With modern PFC power supplies I dont consider those things to be an issue anymore.
If mandatory can't be enforced, when is voluntary going to happen?
My service business is seeing orders for surge protection (SPD) from HVAC contractors, to prevent circuit board damage. Clients are calling with end-use equipment instructions requiring SPD. Never seen this before, much less NEC mandates for SPD wherever AFCI is installed. Shielding against utility excursions & EMP is increasingly difficult, as is adapting xFCI's to electronic warfare of harmonic appliances.With modern PFC power supplies I dont consider those things to be an issue anymore.
Does that include unlisted equip, with no FCC testing, which everyone buys from Amazon?
Did utilities stop charging commercial & industrial customers for non-linear loads, because everyone uses PFC?
Do you specify PFC for lighting, or measure THD, before ignoring neutral CCC's on a balanced Wye per 310.15(E), before ignoring prohibited neutral reductions per 220.61(C), or ignoring the up-sized neutral bus over 1000 volts, per 368.258?
I can learn something from honesty, which may share the proof to support the practice, and teach us both.No I do not specify or measure.
Maybe if I was doing a data center and there were feeders or MWBC's supplying only servers I would give it a closer look. Other than than I cant imagine the stars aligning for it to be an issue with the type of work I do.I can learn something from honesty, which may share the proof to support the practice, and teach us both.
I don't think distortion power factor is as much of a concern to utilities as displacement power factor either.For larger commercial projects no one is buying lights from Amazon. Luminaires are required to be listed and unlisted ones would not pass inspections.
I have never come across a utility that measures and charges for non-linear loads
No I do not specify or measure. Yes I just ignore.
Not any longer. The lighting manufacturers have really got the LED grow lights on point these days. They can make any spectrum of light with different LEDs in one fixture. All of the grow facilities I have designed in the last 3 years have all been LED.Seems to still be common to use HID in grow houses as questions involving HID issues that come up on sites like this often are involving grow houses.
Better lighting qualities for growing plants? IDK but kind of assuming that is the case.