Hello to all, Common grounding electrode (AWG#1) through parts of building. ran into soffit that had 6 ft of 1 inch Flexible metal conduit with bonding bushings on both sides. I was told that you could run a #6 through the flex with the #1 AWG, and tie the #6 to both boding bushings. I do not believe this is correct. Can you please tell me code section that clarifies this, if I am right.
Question #2. The common grounding electrode conductor is being tapped at several locations to bod transformers throughout the building. I was told that it is ok to run the common #1 grounding electrode directly to a bus bar, and come off the bus bar to the next bus bar. My understanding is that a common GEC must be cadwelded or compression spliced without relying on the busbar for continuity of the common GEC. Can you please site a code section that clarifies this? Also I read somewhere, that a common GEC must be minimum #3/0 AWG. Any and all help for the several questions are greatly appreciated. I always have come to this site with questions, as there is great experience here. Thanks much
Question #2. The common grounding electrode conductor is being tapped at several locations to bod transformers throughout the building. I was told that it is ok to run the common #1 grounding electrode directly to a bus bar, and come off the bus bar to the next bus bar. My understanding is that a common GEC must be cadwelded or compression spliced without relying on the busbar for continuity of the common GEC. Can you please site a code section that clarifies this? Also I read somewhere, that a common GEC must be minimum #3/0 AWG. Any and all help for the several questions are greatly appreciated. I always have come to this site with questions, as there is great experience here. Thanks much