1 Brkr- 2 Panels

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Per code can you have one breaker feed two panel boards?

Say a 400A MCB feed two 200A MCB panelboards? Obviously, if allowed, you would run a 400A feeder to a tap or splice box then feed each panel from there.

Or I guess you could run feeder from 400A MCB to panelboard and use a branch breaker in the panelboard to feed the other panel.??
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Per code can you have one breaker feed two panel boards?

Say a 400A MCB feed two 200A MCB panelboards? Obviously, if allowed, you would run a 400A feeder to a tap or splice box then feed each panel from there.
Yes. Follow the 240.21 rules if conductor to individual panel is reduced

Or I guess you could run feeder from 400A MCB to panelboard and use a branch breaker in the panelboard to feed the other panel.??
Yes
 