1 disconnected switch with 2 meter?

Status
Not open for further replies.

defishu

Member
Location
new york
Recently, we designed a job that have a existing switch which is HCP367VJ600 with existing meter, but we actually need 2 panels with 2 meters for the job. So i am wondering if we can reuse that existing switch? Is there any problem? More detail would be very nice. i would really appreciate if you could help me out. BTW the switch is unfused. Thanks.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
IMO, as long as you don't exceed the rating of the switch it cares less whats connected to it.
Conductors would need to be protected at their ampacity.
That said, the devil is in the details. Can you provide a bit more info especially considering its a NF switch.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It would be rare where the utility would permit a disconnect on the line side of their cash register.
 

defishu

Member
Location
new york
IMO, as long as you don't exceed the rating of the switch it cares less whats connected to it.
Conductors would need to be protected at their ampacity.
That said, the devil is in the details. Can you provide a bit more info especially considering its a NF switch.

The problem is our senior engineer said we can not reuse that switch, and i am kinda not trust him...My question is how we know if we can reuse that 600 amp switch mentioned above?
 