We are installing a new transfer switch on an installation that currently has a generator and transfer switch in place.
We want to configure this so that either transfer switch will operate the generator.
The current ATS only has 2 control wires connected to the generator control box. All gauges, meters, etc mounted on the generator control box.
I figure this should be a simple switch leg.
So the question is: Can we simply wire in the alternate ATS control wires in parallel with the existing one, so either one will actuate the gen set? OR would we need to install an isolating relay to do the job?
Additional info: Each ATS is rated 400 Amps. Gen set is rated 107 kVA. Utility transformer is only 75 kVA.
120/240 single phase services.
Comments?