I have a voltage drop question.
I was recently called to a very old high rise building on a voltage drop question. It seems that originally an EM lighting feeder was installed 120/240v 1?3W and revised at some point to 120/208v 1?3W. The feeder is 3#8 awg. cu. RHW to the 6th floor loaded to about 30 amps. The branch is #14 cu. RHW loaded to about 12 amps extended up 5 floors and down 5 floors feeding a single compact flourescent outlet at each floor and two exit signs.
The complaint is that this circuit drops to 90 volts or so while the 120/208 volt service is nominal.
Is there an engineering reason why a 1?3W feeder fed from a 3?4W source would drop more volts than normal? I came up with about 9.4% but we're seeing about 25%.
Thanks in advance.
I have a voltage drop question.
I was recently called to a very old high rise building on a voltage drop question. It seems that originally an EM lighting feeder was installed 120/240v 1?3W and revised at some point to 120/208v 1?3W. The feeder is 3#8 awg. cu. RHW to the 6th floor loaded to about 30 amps. The branch is #14 cu. RHW loaded to about 12 amps extended up 5 floors and down 5 floors feeding a single compact flourescent outlet at each floor and two exit signs.