Can anybody advice me if there's any restriction in the NEC about having a single phase and three phase circuit (wires) on a single conduit?
 
There is no rule that would prohibit having both 1 phase and 3 phase wires in the same conduit. However, there are two related rules. One says that you must de-rate every conductor's ampacity, when there are four or more current-carrying conductors in the same conduit. The other gives a limit of 40% for the amount of the internal area that the conductors are permitted to occupy.
 
First off welcome to the forum.:)

You can place 1 phase and 3 phase circuits in the same raceway but you must also take into account derating if you have more than 3 current carrying condutors in the conduit. Take a look at 310.15(B)(2)(a).

Chris
 
Starter122 said:
Thanks for all your reply. You really make it sound so simple to understand. :smile:

Oh just wait , we all have a way of making it sound not so simple, you just haven't asked the right question yet. :grin:
 
Don't forget about the identification rules in 210.5(C) and, if there is a grounded conductor, the one in 200.6(D).
 