Also, 3 phase gennies do not like being unevenly loaded. In electrical power theory, it cause NPS currents (negative phase sequence). These are bad news and cause stator over heating. In big gennies 3% nps is really bad news and 5% can cause the generator to fail. This isn't the same as saying you must have the phase loads within 5% of each other, but my previous post of keep the phases balanced as best you can is good advice.
this is bad if you have other loads sharing the genset. otherwise, if that single load is to have the genset all for himself, why not?