JArch
- Newaygo, MI USA
Yes, again. I have looked and can not find anything that pertains to what I need.
I am trying to calculate the wattage and load on a three phase system that consists of only single phase loads. All loads are resistive.
I have qty 6 units at 2.6 amps, 536 watts @208
qty 1 unit at 23.2 amps, 4815 watts @208
qty 1 unit at 28.9 amps, 6015 watts @208
qty 2 units at .43 amps, 89.44 watts @208
qty 1 unit at .23 amps, 47.84 watts @208.
The only set up that is making any sense so far is:
L1 L2 L3
268 268
268 268
268 268
268 268
268 268
268 268
2407.5 2407.5
3007.5 3007.5
3007.5 3007.5
89.44
89.44
47.84
______________________________
6445.72 6755 7087 = 20287.72
20287.72/208/1.732 = 56.3 Amps
I need to know amp draw and watt total. Not necessarily related to services in the NEC.
From other threads I've read, I kind of understand that you can't use the 1.732 on the unbalanced part. So do I take the difference from 6445.72 and 7087 to get 641.28 /120 for additional amps on that leg?
I would love someone to figure this out for me and then tell me how to do it on my own.
Thanks in advance!!