Here's a question about single phase to 3 phase conversion that I'm having a little trouble figuring out on my own. I would like to supply a total of 10 single phase, 120V loads that will pull about 43 amps. These loads will be supplied by buss duct plug in breakers. My question is what kind of amperage should i expect on the breaker supplying the buss duct?
I realize somebody posts this same question every week but I just wanted to make sure i understood.
Thanks guys.
Edited to add:
43A (per rack) X 10 (Racks/row) = 430A
120V X 430A X 1.732 = 89.268 KVA 3-phase.
89.268KVA / 208 / 1.732 = 248A per phase going through the main breaker.
This was my first attempt but it seems a little high... should i have divided the 430A by 3?
I realize somebody posts this same question every week but I just wanted to make sure i understood.
Thanks guys.
Edited to add:
43A (per rack) X 10 (Racks/row) = 430A
120V X 430A X 1.732 = 89.268 KVA 3-phase.
89.268KVA / 208 / 1.732 = 248A per phase going through the main breaker.
This was my first attempt but it seems a little high... should i have divided the 430A by 3?