yahya176
Member
- Location
- Stone Mountain,GA
Hi, I hope all is well. I notice some post about the subject matter. However, I'm trying to avoid installing sub panel and main shunt and wanted to know Is it acceptable to use a single pole 120v coil type shunt trip breaker for shunt trip requirements for fire suppression? Do I wire it in across micro switch or on a set of aux contacts on contactor? the I have small restaurant job. In which, the wiring for the hood is needed; (1- Exhaust Fan 120v 1ph, 1-MUA 120v 1ph, 2-Receptacle circuits for 2-fryer and lights under hood). The mechanical contractor only provided 1- micro switch. I understand the MAU, receptacles and lights must be denergized by the closing of micro switch. The exhaust fan must remain on. I have two 120v DP contactors provided for (1) MAU and lights controlled by switch and (2) receptacle circuits on "constant" at the other? The exhaust fan is controlled by separate switch. I hope this helps! I'm just not sure if it is acceptable to d-energize the fire control panel circuit only to fulfill the shunt trip requirements. Please advise me, any information to the subject will be greatly appreciated. Thank you in advance. :?