Since you're on your iPhone I'll assume that you con't have the code book so the answer is 25.
 
I get those question more often than I would imagine and always wonder "why"?
Since the adjusted ampacity might be as low as 13.5 amps, the applications would be limited.
 
Answer depends on how full do you want it:D

Seriously, if it is only a 2 foot or less run, it can have more then was mentioned already
 
Answer depends on how full do you want it:D

Seriously, if it is only a 2 foot or less run, it can have more then was mentioned already
I realize that a conduit run of less than 24" is exempt from the conduit fill ampacity derating, but is it also exempt from the 40% maximum fill rule?
 
There is a difference between what the NEC maximum is and how many you can actually fit. The max number of conductors is a good test question though!
 