How many number 12 THHN can go into 1 inch PVC schedule 40 conduit?
Sent from my iPhone using Tapatalk
Sent from my iPhone using Tapatalk
How many number 12 THHN can go into 1 inch PVC schedule 40 conduit?
Sent from my iPhone using Tapatalk
Did you even look in the code book?How many number 12 THHN can go into 1 inch PVC schedule 40 conduit?
Sent from my iPhone using Tapatalk
I realize that a conduit run of less than 24" is exempt from the conduit fill ampacity derating, but is it also exempt from the 40% maximum fill rule?Answer depends on how full do you want it
Seriously, if it is only a 2 foot or less run, it can have more then was mentioned already
I realize that a conduit run of less than 24" is exempt from the conduit fill ampacity derating, but is it also exempt from the 40% maximum fill rule?
Chapter 9, Table 1, Note 4.
How many number 12 THHN can go into 1 inch PVC schedule 40 conduit?
Sent from my iPhone using Tapatalk
I realize that a conduit run of less than 24" is exempt from the conduit fill ampacity derating, but is it also exempt from the 40% maximum fill rule?