1-room air cond. recpt. installation

Status
Not open for further replies.

watts

New member
question: is a one room a.c. allowable under Nec to be wired in with bedroom recpts that is wired on a 15 amp dedicated circuit. A.C. does not exceed 7.5 amps.

[ August 06, 2003, 01:20 PM: Message edited by: watts ]
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 1-room air cond. recpt. installation

Watts, see 210.23 and 210.23 (A)(1)&(2)

Roger
 