fandi
Senior Member
- Location
- Los Angeles
Hello All,
I wonder what the potential issues would be if:
1) Tie two 4000A 480V switchboards (let's call MSB-1 and MSB-2, separately fed from (2) 3-833kva utility transformers) with a 4000A busduct:
These two are 5ft facing each other. The peak combined loads in 1 year of both MSBs are less than 2000A. To maximize the new Cogen, I'd like to connect the Cogen to both MSBs. Meaning I plan to remove one upstream 3-833kva transformer and tie the two MSBs via an approx 10ft 4000A busduct.
For ground fault protection, I'll remove the neutral disconnect link at the switchboard (let's call MSB-2) that its upstream transformer is being removed. This to avoid the two MSBs to have two different neutrals connected to ground.
2) The Cogen switchboard has its own main 2000A motor operated breaker. Can I tap that 2000A Cogen switchboard directly to the one of the two existing MSBs mentioned above? The Cogen is about 100ft away from the MSBs.
Thanks a lot.
I wonder what the potential issues would be if:
1) Tie two 4000A 480V switchboards (let's call MSB-1 and MSB-2, separately fed from (2) 3-833kva utility transformers) with a 4000A busduct:
These two are 5ft facing each other. The peak combined loads in 1 year of both MSBs are less than 2000A. To maximize the new Cogen, I'd like to connect the Cogen to both MSBs. Meaning I plan to remove one upstream 3-833kva transformer and tie the two MSBs via an approx 10ft 4000A busduct.
For ground fault protection, I'll remove the neutral disconnect link at the switchboard (let's call MSB-2) that its upstream transformer is being removed. This to avoid the two MSBs to have two different neutrals connected to ground.
2) The Cogen switchboard has its own main 2000A motor operated breaker. Can I tap that 2000A Cogen switchboard directly to the one of the two existing MSBs mentioned above? The Cogen is about 100ft away from the MSBs.
Thanks a lot.