1 to 1 transformer serving PLC panel.

Status
Not open for further replies.

11bgrunt

Pragmatist
Location
TEXAS
Occupation
Electric Utility Reliability Coordinator
Plant has 480/277 main service. Many dry types connected Delta-Wye to 208/120. All 3 phase.
There are two PLC panels, installed years apart. These serve HVAC system with many units on the roof.
Voltage from POCO is intentionally reduced 3% during their peak and some of the roof units drop out. EC points to 3kVA 1-1 transformer serving PLC panel.
This isolation transformer is connected 120-N and served by a 75kVA dry type, .
What we measured for voltage at the 1-1, source 118.7 - load 119.8.
Amps; source 7+ - load 2.5.
Temperature of 1-1 running 160F.
Problem at PLC only occurred when POCO reduces voltage at their substation, that is not very far away.
The PLC panel in another part of the plant does not have an isolation transformer and is powered by 120 from the same 75kVA that serves the other PLC panel with the 1-1.
I was on the main when voltage was reduced and POCO never went below 460. Math says around 115 at primary of the 1-1. This should not be a problem.
A similar 1-1 on a different application was tested today. it was running a little hotter with less load but the primary voltage was still lower than secondary.
We could not disconnect to do a TTR.
Why is 1-1 primary lower than 1-1 secondary?
Have engineering ideas changed where years ago an isolation transformer was thought necessary and now the need is not there?
Thanks.
 

Attachments

  • ONE TO ONE.jpg
    ONE TO ONE.jpg
    85.4 KB · Views: 0
170720-2412 EDT

11bgrunt:

I took a typical 500 VA control transformer and measured the input and output voltages at no load. Output was about 4% high under no load. I expect this has been wound to provide about a 1 to 1 ratio at full load.

Find a transformer like the one in your equipment. On your test bench measure the no load output voltage, and calculate the ratio. Then fully load the transformer, and redo the measurements. Report back.

But any load devices designed for an industrial environment, in my opinion, should tolerate voltages down to about 95 V.

.
 
Plant has 480/277 main service. Many dry types connected Delta-Wye to 208/120. All 3 phase.
There are two PLC panels, installed years apart. These serve HVAC system with many units on the roof.
Voltage from POCO is intentionally reduced 3% during their peak and some of the roof units drop out. EC points to 3kVA 1-1 transformer serving PLC panel.
This isolation transformer is connected 120-N and served by a 75kVA dry type, .
What we measured for voltage at the 1-1, source 118.7 - load 119.8.
Amps; source 7+ - load 2.5.
Temperature of 1-1 running 160F.
Problem at PLC only occurred when POCO reduces voltage at their substation, that is not very far away.
The PLC panel in another part of the plant does not have an isolation transformer and is powered by 120 from the same 75kVA that serves the other PLC panel with the 1-1.
I was on the main when voltage was reduced and POCO never went below 460. Math says around 115 at primary of the 1-1. This should not be a problem.
A similar 1-1 on a different application was tested today. it was running a little hotter with less load but the primary voltage was still lower than secondary.
We could not disconnect to do a TTR.
Why is 1-1 primary lower than 1-1 secondary?
Have engineering ideas changed where years ago an isolation transformer was thought necessary and now the need is not there?
Thanks.
Sounds like you have a software or firmware problem, not an electrical problem.
 