Hello everyone,
Perhaps someone out there can help me with this problem. I have a 2000 amp main switchboard with a 600 amp breaker feeding a separate building 150 feet away. The feeders are parallel #350's in a 4" underground pvc conduit. The engineer included a #1 ground to be run with these conductor. I didn't see a landing lug for this egc in the utility (unmetered) side of the switchgear that I was tying into. I called the engineer and he said I probably don't need it. I did call a couple of other EC's and the answer was vague. The inspector called me on this. If I do have to pull the ground in,it will be a good lesson to stick with the print. Thanks for everyones help.
Ken.
Sent from my XT1585 using Tapatalk
Perhaps someone out there can help me with this problem. I have a 2000 amp main switchboard with a 600 amp breaker feeding a separate building 150 feet away. The feeders are parallel #350's in a 4" underground pvc conduit. The engineer included a #1 ground to be run with these conductor. I didn't see a landing lug for this egc in the utility (unmetered) side of the switchgear that I was tying into. I called the engineer and he said I probably don't need it. I did call a couple of other EC's and the answer was vague. The inspector called me on this. If I do have to pull the ground in,it will be a good lesson to stick with the print. Thanks for everyones help.