J Jbeshere Member Location Loxahatchee Fl Dec 28, 2017 #1 Is there anywhere in the code book that can tell me if 10/2 UF can be run in 3/4 PVC
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Dec 28, 2017 #2 Jbeshere said: Is there anywhere in the code book that can tell me if 10/2 UF can be run in 3/4 PVC Click to expand... Art. 340.10(4) states we can use UF as NM cable. Article 334.15(B) & (C) clearly allows sleeving the cable. Chapter 9 notes to the table also infers that if you use cable in conduit you must derate based on....
Jbeshere said: Is there anywhere in the code book that can tell me if 10/2 UF can be run in 3/4 PVC Click to expand... Art. 340.10(4) states we can use UF as NM cable. Article 334.15(B) & (C) clearly allows sleeving the cable. Chapter 9 notes to the table also infers that if you use cable in conduit you must derate based on....
roger Moderator Staff member Location Fl Occupation Retired Electrician Dec 28, 2017 #3 Along with Dennis's post see, 352.22 Roger