Good afternoon all I had an inspective family on a recent house we did scenario is
10/2 NMB feeding an AC condenser rated at a minimum circuit and capacity of 31.5 with a max OCP of 40 .
Inspector is saying I need a number eight He's siting 334.80 which I'm aware of for the old NM but 334.80 specifically states the capacity of types NM , NMC, and NMS does not mention anything about NMB.
What say you guys
Sent from my SM-S906U using Tapatalk
10/2 NMB feeding an AC condenser rated at a minimum circuit and capacity of 31.5 with a max OCP of 40 .
Inspector is saying I need a number eight He's siting 334.80 which I'm aware of for the old NM but 334.80 specifically states the capacity of types NM , NMC, and NMS does not mention anything about NMB.
What say you guys
Sent from my SM-S906U using Tapatalk