Could 10-4 mc ,"black,red,blue,white,green" be used to get single phase 30 amp dryer receptacle and a 120 volt 20 amp receptacle for the washer ? Neutral used for both.
No ,source is single phase. My thinking is that neutral usually has little on it from dryer.Yes if you have a 3 phase source and if you can figure a way to handle tie a 2 pole 30 and single pole 20 together.
No ,source is single phase. My thinking is that neutral usually has little on it from dryer.
Well I agree it would work and very likely be safe but your defiantly on thin ice with the code.
So I would say 310.15 might come into play as you have the potential to cause 50amps to flow on a #10.
No ,source is single phase. My thinking is that neutral usually has little on it from dryer.
Actually dryer motor would only be a few amps . The danger would not be from any normal washer and dryer. But with adaptors someone could missuse the dryer receptacle to carry some other load. With proper use would be no problem as the dryer would never have more than few amps on neutral.The drum motor on the dryer is 120 volt, thus a fair load on the neutral. Don't know the reasoning behind it, unless they have changed it lately. So you would have two 120 volt loads on the neutral, unless you luck out and their one opposite legs. Still would not meet code unless you have an oversized neutral, or it is a three phase feed.
The drum motor on the dryer is 120 volt, thus a fair load on the neutral.
Don't know the reasoning behind it, unless they have changed it lately.
The motor in an electric dryer is a very small percentage of the load.
Only reason i gave it a thought was because i have enough 12-4 in my shed to make the run. Seemed like a waste but just will not use the blue. We simply need and extra washer / dryer and will be a real pain to run it.
So you would have two 120 volt loads on the neutral, unless you luck out and their one opposite legs.
So if you were willing to rewire the dryer to have two plugs, one 240V only and one 120V, so that you could control which leg the 120V dryer loads are fed from, could you make an NEC compliant install?
Cheers, Wayne
ooops 10 ----------you're going to use 12 for an electric dryer?