#10 AWG to #12 AWG

Status
Not open for further replies.

billman1

Member
Although I am inquiring about a Hospital installation I believe my question is just standard practice in any application.

A spec book asks for any run over 100 feet be installed in EMT with a minimum of #10 AWG. Drawings are requesting 15A branch circuits
throughout. Is it code to run #10 AWG the first 100 feet to a pull box and then continue with #12 armored cable to the receptacle locations all about the walls,floors and ceilings? I say no... but I can't convince anyone this comes under the 6' tap rule. Am I wrong?
 
Re: #10 AWG to #12 AWG

billman1,
As long as the branch c.b. is 15amp. you can do that all day long,although some members of this forum have stated that their local inspector made them run #10 thru-out the entire circuit?