B) Tables. Ampacities for conductors rated 0 to 2000 volts shall
be as specified in the Allowable Ampacity Table 310.15(B)(16)
through Table 310.15(B)(19), and Ampacity Table 310.15(B)(20)
and Table 310.15(B)(21) as modified by 310.15(B)(1) through
(B)(7).
The temperature correction and adjustment factors shall be
permitted to be applied to the ampacity for the temperature rating
of the conductor, if the corrected and adjusted ampacity does not
exceed the ampacity for the temperature rating of the termination
in accordance with the provisions of 110.14(C).