one of our jobs has 3 transfomers to be installed in ceiling under 50 kva. per drawing they are all required to be installed with 10' tap rule. The area is small and the xfmrs will need to be installed further than 10'. If I cant install the xfmrs within 10' using 10' foot tap rule can I use he 25' tap rule. The transformer will be 480v 3 phase to 120/240v 3 phase. Should the engineer be notified concerning the 10' rule but either way and can i use the 25' tap rule for transformer install ? Or does the 10' and 25' only apply if i dont install a OPCD on secondary side of xfmr?
10-Foot Secondary Tap Rule [240.21(C)(2)]
Secondary conductors can be run up to 10 ft without overcurrent protection, but they must be installed in accordance with the following requirements: Figure 4
(1) The ampacity of the tap conductor is:
Not less than the computed load in accordance with Article 220, and
Not less than the rating of the device supplied by the tap conductors or the overcurrent protective device at the termination of the tap conductors.
(2) The secondary conductors do not extend beyond the switchboard, panelboard, disconnecting means, or control devices they supply.
(3) The secondary conductors are enclosed in a raceway.
25-Foot Secondary Tap Rule [240.21(C)(6)]
Secondary conductors can be run not over 25 ft without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements: Figure 6
(1) The secondary conductors have an ampacity that (when multiplied by the ratio of the secondary-to-primary voltage) is at least 1/3 of the rating of the overcurrent device protecting the primary of the transformer.
(2) The secondary conductors terminate in a single circuit breaker or set of fuses that have a rating not greater than the conductor ampacity.
(3) The secondary conductors are protected from physical damage.
10-Foot Secondary Tap Rule [240.21(C)(2)]
Secondary conductors can be run up to 10 ft without overcurrent protection, but they must be installed in accordance with the following requirements: Figure 4
(1) The ampacity of the tap conductor is:
Not less than the computed load in accordance with Article 220, and
Not less than the rating of the device supplied by the tap conductors or the overcurrent protective device at the termination of the tap conductors.
(2) The secondary conductors do not extend beyond the switchboard, panelboard, disconnecting means, or control devices they supply.
(3) The secondary conductors are enclosed in a raceway.
25-Foot Secondary Tap Rule [240.21(C)(6)]
Secondary conductors can be run not over 25 ft without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements: Figure 6
(1) The secondary conductors have an ampacity that (when multiplied by the ratio of the secondary-to-primary voltage) is at least 1/3 of the rating of the overcurrent device protecting the primary of the transformer.
(2) The secondary conductors terminate in a single circuit breaker or set of fuses that have a rating not greater than the conductor ampacity.
(3) The secondary conductors are protected from physical damage.