I would agree based on the wording, that the answer is YES, a 10' tap does NOT have to land on a OCPD. However it could not be a panelboard due to 408.36. perhaps it could be something like a lighting control panel or a meter center.Yes or No? Tap conductors 10 feet or less do NOT have to land on overcorrect protection.
It is my understanding that the answer is Yes
You can't tap a tap either so it still would limit you to very few possibilities - I can't think of any at the moment. Like you mentioned for panelboards most anything that is not already an overcurrent device would likely require certain overcurrent protection ahead of it anyway. If said item is rated for same ampacity as your feeder- you don't exactly have need for a feeder tap to begin with.I would agree based on the wording, that the answer is YES, a 10' tap does NOT have to land on a OCPD. However it could not be a panelboard due to 408.36. perhaps it could be something like a lighting control panel or a meter center.
IIRC, the 10' wording was changed a few cycles ago, but for some reason they seemed to dance around clearly stating that the tap must terminate on a single OCPD like they say in the 25' rule.
Probably one of those judgement calls. In general a cable is not a raceway though.I was looking for information on 10 ft tap rule approved raceway . Would Mc cable of 1 ort be an approved raceway .
Probably one of those judgement calls. In general a cable is not a raceway though.
In addition to the items I said in post #2, a switchboard is another item that has no requirement to be protected at it's rating by an OCPDYou can't tap a tap either so it still would limit you to very few possibilities - I can't think of any at the moment. Like you mentioned for panelboards most anything that is not already an overcurrent device would likely require certain overcurrent protection ahead of it anyway. If said item is rated for same ampacity as your feeder- you don't exactly have need for a feeder tap to begin with.
For a Temporary feed to a disconnectI was looking for information on 10 ft tap rule approved raceway . Would Mc cable of 1 ort be an approved raceway .
If the word raceway is what is used then that excludes cables, unless there is more wording that allows otherwise.How would MC cable be different than FMC conduit, in terms of its physical function? Only difference is factory-wired vs field-wired, yet FMC conduit would clearly count as a raceway in this context.
Panelboards must be protected at no more than their rating, didn't check but probably is what is mentioned in 408.36. Therefore you can't feed a main lug panel with a feeder tap, you would need a main breaker panel or other proper overcurrent protection ahead of the panelboard, or back fed main with proper hold down kit is equivalent to a main breaker panel.Back to the OP, I was thinking of a small, main lug panel. But I have not read 408.36 yet
Not less than the rating of the device supplied by the tap conductors or not less than the rating of the overcurrent protective device at the termination of the tap conductors.
Not less than the rating of the equipment containing an overcurrent device(s) supplied by the tap conductors or not less than the rating of the overcurrent protective device at the termination of the tap conductors.
The previous code language allowed the tap conductor ampacity to be rated no less than the “device” supplied by the tap conductors. This was misleading and opened the door to the idea that a tap conductor could be without any overcurrent protection at the load end of the conductor if it supplied a device rather than an overcurrent device.
240.21 feeder tap rules cover conductors tapped from a feeder. If what you are describing is all ahead of the service disconnecting means they don't fall under 240.21 and are not feeder taps. They are simply taps made to service conductors. There is no "tap rules" for service conductors they are all presumed to have no protection ahead of them that limits how much current can flow.So a tap conductor could not supply a meter base, then a panel with overcorrect protection directly next to it?