10 Foot Tap Rule Question

Status
Not open for further replies.

darren71

Member
I have a question about the application of the 10 foot tap rule (240.21 (B) (1)). I have two RTU's I need to power, one requiring 150 A, the other 40 A at 208V 3 phase. There is an existing 2500 Amp switchgear that is full up (capacity wise, not ampacity wise) that I would like to tap off from to a couple of fusible disconnect switches within 10 feet. My confusion stems from part (4) of the article referenced above that states that if the tap conductors leave the enclosure from where they are tapped, they have to be no less than a tenth of the ampacity of the OCPD of the line side (in this case, 2500 Amps). Does this mean I have to have conductors sized for 250 A, since the conductors leave the switchgear, go a few feet in conduit, to disconnect switches?
 
Re: 10 Foot Tap Rule Question

Yes that is correct.

Also if you run an EGC it will need to be 350 CU or 600 AL from the service gear to the disconnects.
 
Re: 10 Foot Tap Rule Question

Thinking about this more I would say you better plan on two 200 amp disconnects one with fuse reducers in it to get the 40 amp fuses in.

I doubt you can get a 60 amp disconnect with lugs large enough and space to bend 250 amp conductors.
 
Re: 10 Foot Tap Rule Question

Originally posted by iwire:
Also if you run an EGC it will need to be 350 CU or 600 AL from the service gear to the disconnects.
Except 250.122(A) limits the EGC to not exceed the circuit conductor size.

[ September 28, 2004, 08:42 AM: Message edited by: engy ]
 
Re: 10 Foot Tap Rule Question

An "EGC" is an equipment grounding conductor. See the definitions in Article 100.

Steve
 
Re: 10 Foot Tap Rule Question

Do you have the alternative of taping off one of the existing feeders? In other words, instead of connecting directly to the switchgear (with its 2500 amp Main), can you tap off downstream of one of the existing breakers? If an existing breaker is listed for double lugs, that could solve your problem. Or perhaps you have an existing breaker that feeds a conveniently located panel that, in turn, has feed-through lugs that you can use. There are other possibilities for tap points.

Finally, can you install a new sub-panel, disconnect an existing circuit from its breaker (thus creating a spare breaker on the switchgear), reconnect that circuit to the new sub-panel, and then power the sub-panel from the (newly created) spare?
 
Re: 10 Foot Tap Rule Question

Originally posted by engy:
Originally posted by iwire:
Also if you run an ECG it will need to be 350 CU or 600 AL from the service gear to the disconnects.
Except 250.122(A) limits the ECG to not exceed the circuit conductor size.
Good point, I did not really think about the size of the ungrounded conductors he would be running. :)
 