I have a question about the application of the 10 foot tap rule (240.21 (B) (1)). I have two RTU's I need to power, one requiring 150 A, the other 40 A at 208V 3 phase. There is an existing 2500 Amp switchgear that is full up (capacity wise, not ampacity wise) that I would like to tap off from to a couple of fusible disconnect switches within 10 feet. My confusion stems from part (4) of the article referenced above that states that if the tap conductors leave the enclosure from where they are tapped, they have to be no less than a tenth of the ampacity of the OCPD of the line side (in this case, 2500 Amps). Does this mean I have to have conductors sized for 250 A, since the conductors leave the switchgear, go a few feet in conduit, to disconnect switches?