10-32 Log #2151 NEC-P10 Final Action: Accept in Principle
(240.21(B)(1))
________________________________________________________________
Submitter: Phil Simmons, Simmons Electrical Services
Recommendation: Revise text to read as follows:
(1) Taps Not over 3 m (10 ft) Long. If the length of the tap conductors does
not exceed 3 m (10 ft) and the tap conductors comply with all of the following:
(1) The ampacity of the tap conductors is
a. Not less than the combined calculated loads on the circuits supplied by the
tap conductors, and
b. Not less than the rating of the equipment containing an overcurrent
device(s) supplied by the tap conductors or not less than the rating of the
overcurrent protective device at the termination of the tap conductors.
(2) The tap conductors do not extend beyond the switchboard, panelboard,
disconnecting means, or control devices they supply.
(3) Except at the point of connection to the feeder, the tap conductors are
enclosed in a raceway, which shall extend from the tap to the enclosure of an
enclosed switchboard, panelboard, or control devices, or to the back of an open
switchboard.
Substantiation: This proposal is intended to clarify the application of the
existing requirement and state the specific type of device as an overcurrent
device. This clarification is needed since a conductor fits within the definition
of “device” in Article 100. The submitter is quite confident such an application
or interpretation would not meet the intention of the Code Panel who is
responsible for this Article.
The term “equipment containing an overcurrent device(s)” could be a main-lug
panelboard, a fusible switch, a switchboard or a motor control center.
Panel Meeting Action: Accept in Principle
Add exception after 240.21(B)(1)(b) and revise text to read as follows:
(1) Taps Not over 3 m (10 ft) Long. If the length of the tap conductors does
not exceed 3 m (10 ft) and the tap conductors comply with all of the following:
(1) The ampacity of the tap conductors is
a. Not less than the combined calculated loads on the circuits supplied by the
tap conductors, and
b. Not less than the rating of the equipment containing an overcurrent
device(s) supplied by the tap conductors or not less than the rating of the
overcurrent protective device at the termination of the tap conductors.
Exception: Listed surge protective device(s) (SPD) installed in accordance with
285.23 or 285.24.
(2) The tap conductors do not extend beyond the switchboard, panelboard,
disconnecting means, or control devices they supply.
(3) Except at the point of connection to the feeder, the tap conductors are
enclosed in a raceway, which shall extend from the tap to the enclosure of an
enclosed switchboard, panelboard, or control devices, or to the back of an open
switchboard.
Panel Statement: The panel added a new exception following 240.21(B)(1)(b)
to address the installation of surge protective device(s) (SPD).
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11