Grouch1980
Senior Member
- Location
- New York, NY
I'm following the 2008 NEC code cycle... my question is regarding the 10 foot tap rule in section 240.21(B)(1).
I always have the tap conductors terminate in a single OCPD in previous projects, whenever i needed a tap.
I'm working on a project now where I'm showing the tap conductors terminating in a switch & fuse board, with multiple switches. However, I'd like to avoid having a main switch. I believe this is possible, is that correct? The section doesn't specifically say the tap conductors have to terminate in a SINGLE device, as (B)(2) states for the 25 foot tap rule.
As long as the tap conductors terminate in a "device" (the switch & fuse board), where the ampacity of the tap conductors is not less than the rating of that device, I should be fine? For example, 100 amp tap conductors terminating in a main lug only board rated for 100 amps is code compliant? I'm also aware that the calculated load of the circuits fed by the tap conductors cannot exceed the tap conductor ampacity.
Thanks!
I always have the tap conductors terminate in a single OCPD in previous projects, whenever i needed a tap.
I'm working on a project now where I'm showing the tap conductors terminating in a switch & fuse board, with multiple switches. However, I'd like to avoid having a main switch. I believe this is possible, is that correct? The section doesn't specifically say the tap conductors have to terminate in a SINGLE device, as (B)(2) states for the 25 foot tap rule.
As long as the tap conductors terminate in a "device" (the switch & fuse board), where the ampacity of the tap conductors is not less than the rating of that device, I should be fine? For example, 100 amp tap conductors terminating in a main lug only board rated for 100 amps is code compliant? I'm also aware that the calculated load of the circuits fed by the tap conductors cannot exceed the tap conductor ampacity.
Thanks!
Last edited: