Can I run 8 feet of 10 guage copper wire safely on a 40 amp breaker? Please email me at saiprem2@hotmail.com Thanks.
Do not forget as BPH pointed out motor loads may have much larger breakers then the rating of the conductors feeding them.Originally posted by mkbuck:
Read 240.4(D)
The overcurrent protection shall not exceed 30 amperes for a 10 AWG conductor, unless covered by the conditions described in 240.4(E),(F) or (G).