Re: 10 kva transformer which is best? fuses or circuit brea
It is of my opinion that with the limited information that you have provided a specific answer is dificult to give.
To start out with, as a rule of thumb, you can expect the inrush of a 150degC 10kva dry type transformer to be about 20x the FLA. This increases for 115degC, 80degC, and K-factor transformers.
Also, the instantaneous or magnetic trip value or highest adjustable trip value is 10X the breaker rating.
Then the question is if the OCPD used, either fuse or breaker, will allow the transformer to be energized with out tripping or blowing. Also, is it the maximum rating that is allowed by the NEC for the specific installation.
You didn't say if it was a single with a two or three wire single phase secondary or three phase with a 3w or 4w secondary which will determine if secondary protection is required and the primary protection rating. Another consideration is if secondary protection is provided and how far is the primary protective device is located from it.
Table 450.3(B) shows the latitude that is provided when 240.21 (3) Taps Supplying a Transformer (primary plus secondary not over 25 ft. long.