Pierre, Pierre, Pierre .... tsk, tsk.
LOOK AT THE THREAD TITLE !!
We are dealing with a
10 kw heat load here!
The 54 Amp rating
already has been adjusted by the required 125%
10,000 watts divided by 230 Volts = 43.4 Amps
Multiplied by 125% =
54.25 Amps
You are adding this factor in a 2nd time here ....
Edit to add:
If you were to use 240 Volts for your calculation, you end up with 52 Amps, then you can allow a couple more amps for the blower motor, making the minumum circuit ampacity come out to 54 as the nameplate stipulates.