M mannyb Senior Member Location Florida Occupation Electrician Mar 11, 2021 #1 ALL wiring to be installed in conduit. MC allowed max lenght 10' for lighting. I ask question because I show on drawings to have 1x8' and 1x4' fixtures running end to end. is it permitted to run circuit thru fixtues?
ALL wiring to be installed in conduit. MC allowed max lenght 10' for lighting. I ask question because I show on drawings to have 1x8' and 1x4' fixtures running end to end. is it permitted to run circuit thru fixtues?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 11, 2021 #2 If the fixture is listed for pass thru then you can run thru the fixture
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 11, 2021 #3 Here is a Mike Holt graphic
M mannyb Senior Member Location Florida Occupation Electrician Mar 11, 2021 #4 Dennis Alwon said: Here is a Mike Holt graphic View attachment 2555724 Click to expand... Fixtures are LDS8 and this is off spec sheet. You are right to say as long as they are approved Installation • Suitable for surface, pendant, grid and chain mounting. • Accepts optional plug-in wiring feature for continuous row installation. • Alignment couplers furnished for continuous row installation.
Dennis Alwon said: Here is a Mike Holt graphic View attachment 2555724 Click to expand... Fixtures are LDS8 and this is off spec sheet. You are right to say as long as they are approved Installation • Suitable for surface, pendant, grid and chain mounting. • Accepts optional plug-in wiring feature for continuous row installation. • Alignment couplers furnished for continuous row installation.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 11, 2021 #5 Sounds like you are good to go