10' tap rule

Status
Not open for further replies.

mannyb

Senior Member
Location
Florida
Occupation
Electrician
We have an 800a feeder that we plan on tapping off of for a 10kva transformer. Its been a while on tap but using the 10' tap rule would the wire tap size need to be able to carry 80a ?
 
There is no 10' tap rule for transformers.

240.21(B)(3) for the feeder supplying the transformer and 240.21(C) for the secondary conductors from the transformer. 240.21(B)(3) applies to the feeder on the primary side of the transformer and the total tap length of secondary and primary. The rules for protecting the secondary conductors are in 240.21(C). If the feeder supplying the transformer is not a tap, then only 240.21(C) applies to the secondary conductors.

And remember, there is no rounding up with OC when protecting conductors at 800A or over and when protecting a tap conductor.

The exception being, if you provide protection between the tap and the transformer, as in, a 800A feeder, 80A tap, to a fuse disconnect that is 80A or less, then to a transformer that is adequately protected by it. The conductors for the 80A tap must be of equal or higher ampacity. So #3 AWG Cu or greater.

The exception is a design that makes the transformer's feeder after the OC of the tap, which means it is no longer a transformer tap.
 
Are you tapping off of an 800A conductor to feed a transformer primary side OCPD? Use 240.21(B)(1) or (2).
Or
Are you tapping off an 800A conductor and feeding a transformer without dedicated primary side protective device? Use 240.21(B)(3).
 
another question, being 800 amp it is obviously parallel conductors, have you accounted for parallel taps ? you can't just tap one set of conductors.
 
Voltage wasn't mentioned, but I don't see how an 800A ocpd would protect a 10kVA transformer..
Maybe I'm the only one who thought it was obvious, but I thought that the transformer is the load being supplied by the tap. And that the unmentioned OCPD for the load is obviously less than 80A, hence the question if the tap conductors need to be sized for 80A.
 
Me either, but the OP doesn't mention any OC other than 800A.
The OP mentioned the 10' tap rule (240.21(B)(1)), which requires an OCPD (or equipment containing an OCPD) at the end of the tap.

I don't think there as any conceivable way that 240.21(B)(3) would apply to the installation.
 
The OP mentioned the 10' tap rule (240.21(B)(1)), which requires an OCPD (or equipment containing an OCPD) at the end of the tap.

I don't think there as any conceivable way that 240.21(B)(3) would apply to the installation.
I agree it is unlikely.
For the most part it is hard to conceive a 240.21(B)(3) compliant installation except where small transformers are being installed on street/yard lighting circuits to either power the light itself or a convenience outlet. I think I was involved in one installation for pole mounted power boosters for 'cable TV' distribution.
 
The OP mentioned the 10' tap rule (240.21(B)(1)), which requires an OCPD (or equipment containing an OCPD) at the end of the tap.

I don't think there as any conceivable way that 240.21(B)(3) would apply to the installation.

I also agree that there is no conceivable way to make a complaint install applying 240.21(B)(3) to the OP's situation. And as acrwc10 pointed out, there is the hurdle of possible parallel runs.
 