10-ft feeder tap rule [240.21(B)(1)] ? You don't have to install an OCPD at the tap point of a feeder tap if its length doesn't exceed 10 ft and if it meets the following requirements
The ampacity of the tap conductor is not less than the computed load in accordance with Art. 220, and not less than the rating of the device supplied by the tap conductors or the OCPD at the termination of the tap conductors.
The tap conductors aren't extended beyond the equipment they supply.
The tap conductors are installed in a raceway if they leave the enclosure.
The tap conductors have an ampacity of no less than 10% of the ampacity of the OCPD from which the conductors are tapped.
My question is,
What does it mean by the tap conductors can't extend beyond the equipment they supply?
If a 400a fused disconnect was tapped from a 2000 amp buss with 500 mcm
Thhn within 10', would this installation be acceptable or not.
I'm reading this to mean that the definition of the tap conductor ends at the line side of the 400a Fused Disconnect.
The ampacity of the tap conductor is not less than the computed load in accordance with Art. 220, and not less than the rating of the device supplied by the tap conductors or the OCPD at the termination of the tap conductors.
The tap conductors aren't extended beyond the equipment they supply.
The tap conductors are installed in a raceway if they leave the enclosure.
The tap conductors have an ampacity of no less than 10% of the ampacity of the OCPD from which the conductors are tapped.
My question is,
What does it mean by the tap conductors can't extend beyond the equipment they supply?
If a 400a fused disconnect was tapped from a 2000 amp buss with 500 mcm
Thhn within 10', would this installation be acceptable or not.
I'm reading this to mean that the definition of the tap conductor ends at the line side of the 400a Fused Disconnect.