10 volt DC light control

Status
Not open for further replies.
question under what class does 10 volt DC controled ballast fall under or if not defined by current codes. The ballast is a Universal ES-1-CFH-42/32/26-UNV-HT-DIM-10. Thank You
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
If you're talking about the control wiring I'm going to say use class 1 and combine it with the other conductors. Seems the on/off switch and dimming control has line voltage on it as of course does the ballast. Control wiring connects to both within the same enclosures. I see no mention of CL2 or CL3 wiring being permitted which means that it is class 1.

To be sure you could give Universal tech support a call.

-Hal
 