I am working on a school that is increasing it's welding training area from 7 welding stations to 10 welding stations. The instructor says that all 10 may be in use simultaneously. We are upgrading the existing ventilation also. I am looking for some provisions, in the 2002 NEC, that will allow me to prove a non-continuous load. I guess I am looking for a clarification of Article 630.11 (B)
Example: Welders have an input of 45.5 amp
Using Article 630.11 (B), does this mean...
45.5 x2 (100% of the 2 largest welders)= 91
45.5 x.85 (85% of the 3rd largest welder)= 38.7
45.5 x.70 (70% of the 4th largest welder)= 31.9
45.5 x.60 x6 (60% of all remaining weldes)= 163.8
Then 10 welders would yield a total of 325.4 amps?
Thank you for your help,
- Randy