Anyone heard about this? Here in NJ effective January 1, 2019 all newly installed battery operated smoke alarms must be contain a 10 year sealed battery. This will keep people from removing the batteries and defeating the purpose of the alarms. Do any other states currently have this requirement?
Effective Immediately!!!
All battery smoke detectors must be the 10 year sealed battery units. No
other detectors other than those listed below will be approved.
§ 5:70-4.19 Smoke alarms for one- and two-family dwellings; carbon monoxide alarms; and portable fire
extinguishers
(a) In one- and two-family or attached single family dwellings subject to the requirements of N.J.A.C.
5:70-2.3, smoke alarms shall be installed as follows:
1. On each level of the premises; and
2. Outside of each separate sleeping area.
(b) The smoke alarms required in (a) above shall be located and maintained in accordance with NFPA
72.
1 . The alarms shall not be required to be interconnected.
(c) Ten-year sealed battery-powered single station smoke alarms shall be installed and shall be listed in
accordance with ANSI/UL 217, incorporated herein by reference. However, A/C-powered single or
multiple-station smoke alarms installed as part of the original construction or rehabilitation project shall
not be replaced with battery-powered smoke alarms. The effective date of this subsection shall be January
1, 2019.
1. A/C-powered smoke alarms shall be accepted as meeting the requirements of this section.